Fronius Verto
Your photovoltaic system can do more
Fronius Verto, the adaptable inverter for small businesses, agriculture and apartment blocks. Its flexibility makes it the perfect choice both for the construction of a new PV system and for an extension. With integrated safety features and innovative shading management, the Fronius Verto ensures optimum operation. Sector coupling is made possible by our flexible inverter with its open interfaces. Charging boxes such as Fronius Wattpilot or consumption controllers such as Fronius Ohmpilot can thus be easily integrated.
Technical Data
Input Data
| Number of MPP trackers | 4 |
Feed-in start voltage (Udc start) | 150 V |
Nominal input voltage (Udc,r) | 600 V |
| Min. MPP voltage (U mpp min) | 150 V |
| Max. MPP voltage (U mpp max) | 870 V |
Max. PV generator power (Pdc max) | 40,5 kWpeak |
Max. input current string (Idc max, String) | 28 A |
Output Data
AC nominal output (Pac,r) | 27 kW |
Max. output power (Pac max) | 27 kVA |
| Max. grid power demand | 27 kVA |
| Max. AC output current | 53,7 A |
Grid connection (Uac,r) | 380/220V 400/230V 440/254V 480/277V |
| Grid connection (Uac,r) | 3~ (N)PE 380/220 3~ (N)PE 400/230 |
AC voltage range (Umin - Umax) | 176-528V |
| Power factor range | 0-1 ind./cap. |
General Data
| Dimension / width | 574 mm |
| Dimension / height | 865 mm |
| Dimension / depth | 279 mm |
| Weight | 38,9 kg |
| Weight incl. packaging | 49,6 kg |
| Degree of protection | IP66 |
| Protection class | 1 |
| Overvoltage category (DC / AC) | 2/3 |
| Night-time consumption | 16W |
| Inverter design | Trafolos |
| Cooling | Active air cooling |
| Installation | Indoor and outdoor installation |
| Ambient temperature range | -40°C - +60°C |
Overvoltage protection 1) | Type 1+2 or type 2 |
| Permitted humidity | 0 - 100% |
| Sound emissions | 54,6 dB(A) |
Efficiency
| Max. efficiency | 97,47 % |
| European efficiency (ηEU) | 97,36 % |
| MPP adaptation efficiency | > 99,9 % |
Protection Devices
| DC disconnector | Integrated |
| Integral RCMU | Integrated |
Interfaces
| Ethernet LAN RJ45 | 10/100 Mbit max. 100 m Fronius Solar.web, Modbus TCP, JSON |
| 6x digital in/out + 6x digital in | Connection to ripple control receivers, energy management, load management |
| Emergency stop (WSD) | Integrated |
| Datalogger and web server | Integrated |
| WLAN | Fronius Solar.web, Modbus TCP, JSON, 802.11b/g |
| 2x RS485 | Modbus RTU SunSpec (third-party provider) / Fronius Smart Meter |
AC Connection Technology
| Conductor material | Al and Cu |
DC Connection Technology
| Connection terminals | DC direct connection Stäubli Multi Contact MC4 |
Technical Data
| Cable gland | AC: M32 (Ø12-24.5 mm) Prepared for Option 1: M50 cable gland (Ø10-35 mm) Option 2: 1.5" conduit connection PE & data communication: 2 x M32 (3xØ4.9-5.5 mm + 3xØ6.7-8.5 mm) |
| Grid connection | (N)PE |
Dynamic Peak Manager
Active Cooling
Active cooling technology relies on one or more fans, which not only avoid hot spots, but also regulate the air circulation inside the inverter, thus keeping the temperature of the power electronics low. This has a positive effect on the service life of the devices, optimises yields and reduces costs. At Fronius, active cooling is supplied as standard in all devices.Clear HTML version of the operating instructions. Mobile and optimised for every device.